NOTICE:

Information provided in these message boards is not necessarily the opinion of Sprung Services, Inc.  These discussion boards are provided as a free service to the boiler operations community to promote the free exchange of ideas and to provide assistance from one boiler operator to another as they see fit. 

Sprung Services accepts no responsibility nor guarantees the accuracy of any posts in these message boards.

NOTICE:

Information provided in these message boards is not necessarily the opinion of Sprung Services, Inc.  These discussion boards are provided as a free service to the boiler operations community to promote the free exchange of ideas and to provide assistance from one boiler operator to another as they see fit. 

Sprung Services accepts no responsibility nor guarantees the accuracy of any posts in these message boards.

Clock Time in the Forum by Wagner
To Whom It May Concern: It appears that the running clock time in these forums is off by one hour; ...
RE: Differential Settings on Operating Pressure Control by Wagner
Dear Reed: In response to your questions: The school boiler that I am operating did not have much ...
RE: Water Column by Reed
I'm glad it took me a while to get to this question and Bob beat me to it. The answer is better tha...
RE: boiler licensing juristictions by Reed
These would also be of interest (from Bob's link): (13) hot water heating and other hot liquid bo...
RE: Differential Settings on Operating Pressure Control by Reed
Richard, I think I see your concern here. First, I wouldn't worry about a stable steam pressure....
RE: Differential Settings on Operating Pressure Control by Wagner
Dear Reed: Thank you very much for the thorough reply to my question about setting the subtractive ...
RE: Differential Settings on Operating Pressure Control by Reed
Richard, First of all, I would like to apologize for not getting back to you for so long.  I...
RE: Water Column by RBob
Hi Steve: .433 pounds per square inch per foot of water. Another way: A 'column' of water that...
RE: boiler licensing juristictions by RBob
Hi Steve: I think that your question might better be worded as "What boilers are exempt from operat...
Water Column by stevenaudette
  In class we were given the value for a water column. 0.4433…??? I’m looking for the exa...
Sprung Services Public Forums
Subject: Water level return after blowdown--
Prev Next
You are not authorized to post a reply.

Author Messages
RBobUser is Offline
Intermediate Member
Intermediate Member
Posts:31

12/14/2008 5:28 PM  

Any official word on what would constitute "too long" to wait for the water level to return after a water column blowdown?

Or is this one of those "reasonable and prudent" kinda things?

I mean, I think that we could all agree that a minute might be too long...

But what about 30 seconds?  15 seconds?

 

Maybe I'll add another Q here, too...

How are you checking your LWCO?  I  (Unless I've got a pretty good load, and can't stand an interruption) like to secure the feed...and wait and watch---

 

 

ReedUser is Offline
Veteran Member
Veteran Member
Posts:462

12/14/2008 6:13 PM  

I'm not aware of an official answer to this, but I can say with confidence that 30 seconds is way too long.  15 seconds is too long as well.

It depends upon the size of the boiler and configuration of the water column piping.  If the water has to travel a longer distance it could take a little longer, but most of the time it should be almost immediate.

The way to be sure about this for your boiler is to test it right after you have the boiler and water column inspected.  If the water column is completely clear and it takes 4 seconds, then 4 or 5 seconds should be acceptable to your boiler.  10 seconds means there is starting to be a problem.  15 seconds means shut it down and take the column piping apart.

Thanks for posting.

-Reed


Reed Sprung
Sprung Services, Inc.
ReedUser is Offline
Veteran Member
Veteran Member
Posts:462

12/14/2008 6:19 PM  

LWCOs should be blown down daily  with the boiler running to see if the boiler shuts down like it's supposed to (without pressing the LWCO bypass button if you have one).  If you just can't/won't tolerate having your boiler go down during this test everyday, then do it as often as you possibly can.  Our official recommendation is to let it shut the boiler off every day.

If you blow down the LWCO just to get the sludge out, you are only performing half of the test (the other half is to prove the burner will cut out).

Bob - Does this cover the 2nd question?  I'm not sure.

This answer refers to high-pressure boilers.  For low-pressure boilers, do this weekly.

Reed


Reed Sprung
Sprung Services, Inc.
RBobUser is Offline
Intermediate Member
Intermediate Member
Posts:31

12/15/2008 8:32 AM  
Thanks for the reply, Reed.

Is it a requirement to actually let the burner drop on a lwco test?

And I've heard that the evaporative test (secure the feed and let her drop)is preferred, but just doing a blow-down is acceptable, too?

-bob
ReedUser is Offline
Veteran Member
Veteran Member
Posts:462

12/15/2008 7:52 PM  

Bob,

This type of thing would be difficult to enforce, so things like this are ASME recommendations rather than requirements.  Letting the boiler trip is strongly recommended (otherwise it is not a test, it's just removing mud), although an inspector will not come in and force you to do this. 

It is assumed that a good operator will attempt to do this in something like the frequency recommended in the code.

Keep posting!

Reed


Reed Sprung
Sprung Services, Inc.
ReedUser is Offline
Veteran Member
Veteran Member
Posts:462

12/15/2008 7:57 PM  

Bob,

An evaporation test is recommended once per year.  If your LWCO is a little "sticky" it may shut the boiler down during a blowdown test, but hang up if the water level dropped more slowly like it really would if there were a problem.  An evaporation test is done to make sure the LWCO will work in that type of situation.  However, it is a more involved test and is only recommended annually.

Reed

 


Reed Sprung
Sprung Services, Inc.