Information provided in these message boards is not necessarily the opinion of Sprung Services, Inc.  These discussion boards are provided as a free service to the boiler operations community to promote the free exchange of ideas and to provide assistance from one boiler operator to another as they see fit. 

Sprung Services accepts no responsibility nor guarantees the accuracy of any posts in these message boards.

NOTICE:

Information provided in these message boards is not necessarily the opinion of Sprung Services, Inc.  These discussion boards are provided as a free service to the boiler operations community to promote the free exchange of ideas and to provide assistance from one boiler operator to another as they see fit. 

Sprung Services accepts no responsibility nor guarantees the accuracy of any posts in these message boards.

Clock Time in the Forum by Wagner
To Whom It May Concern: It appears that the running clock time in these forums is off by one hour; ...
RE: Differential Settings on Operating Pressure Control by Wagner
Dear Reed: In response to your questions: The school boiler that I am operating did not have much ...
RE: Water Column by Reed
I'm glad it took me a while to get to this question and Bob beat me to it. The answer is better tha...
RE: boiler licensing juristictions by Reed
These would also be of interest (from Bob's link): (13) hot water heating and other hot liquid bo...
RE: Differential Settings on Operating Pressure Control by Reed
Richard, I think I see your concern here. First, I wouldn't worry about a stable steam pressure....
RE: Differential Settings on Operating Pressure Control by Wagner
Dear Reed: Thank you very much for the thorough reply to my question about setting the subtractive ...
RE: Differential Settings on Operating Pressure Control by Reed
Richard, First of all, I would like to apologize for not getting back to you for so long.  I...
RE: Water Column by RBob
Hi Steve: .433 pounds per square inch per foot of water. Another way: A 'column' of water that...
RE: boiler licensing juristictions by RBob
Hi Steve: I think that your question might better be worded as "What boilers are exempt from operat...
Water Column by stevenaudette
  In class we were given the value for a water column. 0.4433…??? I’m looking for the exa...
Sprung Services Public Forums
Subject: conversion rates
Prev Next
You are not authorized to post a reply.

Author Messages
dennisUser is Offline
Novice Member
Novice Member
Posts:1

04/06/2009 4:32 PM  

reed on the state liscence app they want to know past experiance in btu.  what is the conversion from mw or kw to btu?

ReedUser is Offline
Veteran Member
Veteran Member
Posts:462

04/07/2009 8:32 PM  

Dennis,

Thanks for the question.  The main conversion you will need for your experience affidavit will be Megawatts (or Kilowatts) to boiler horsepower, because the application requires a BHP or a boiler horsepower unit (a megawatt conversion is obviously for a large plant).

Although it lists btu input (they mean btu/hr) at one point on the form, horsepower is preferred.

Boiler Horsepower is a confusing issue, because a boiler horsepower is not the same as mechanical or other types of horsepower. 

For example:

1 Horsepower = 746 Watts = 2,546 btu/hour

Although this conversion is true for mechanical and other types of horsepower, it is not correct for boiler horsepower.

1 Boiler Horsepower is the amount of power required to change 34.5 pounds of water to 34.5 pounds of steam at 212 degrees Fahrenheit in one hour.

Each pound of steam requires the addition of 970.4 btu/lb of energy (latent heat at 212 Fahrenheit) to make the change from water to steam.  Therefore, in one hour a boiler must add 33,478.8 btu's (970.4 x 34.5) to change 34.5 pounds of water to 34.5 pounds of steam.

So, the conversion for boiler horsepower is:

1 Boiler Horsepower = 33,478.8 btu/hr. (instead of 2,546 btu/hr - huge difference)

Now, 1 Megawatt = 3,414,000 btu/hr

1 Megawatt (3,414,000 btu/hr) divided by 1 Boiler Horsepower (33,478.8 btu/hr) = 101.97 Boiler Horsepower per Megawatt.

In other words, 1 Megawatt = 101.97 Boiler Horsepower

Just multiply the number of Megawatts by 101.97 and you have your answer.  Again, this will not work for other types of horsepower.  Only boiler horsepower (BHP).

If you want to find the btu/hr input, it should be on the burner.  The conversion factor the state uses is 1 BHP = 67,000 btu/hr input.

I know I gave alot of detail here, but the fact that horsepower and boiler horsepower are 2 totally different numbers can be confusing if you don't know the details.

-Reed

P.S.  I couldn't find this conversion anywhere, so I had to derive it on the fly for you.  I double-checked my math, but you should probably check my math too, just in case. 


Reed Sprung
Sprung Services, Inc.
ReedUser is Offline
Veteran Member
Veteran Member
Posts:462

04/07/2009 8:49 PM  

By the way, the conversion above is only for large power plants.  If you need to find the horsepower for licensing purposes for process or heating plants, just find the square feet of heating surface and divide by 10.  This number should be on the name plate or in the boiler documentation.  This is the preferred calculation.  It isn't very acurate, but it is an easy calculation and it's close enough for licensing purposes.

If you can't find the heating surface number, find the btu/hr input and divide by 67,000.