Information provided in these message boards is not necessarily the opinion of Sprung Services, Inc.  These discussion boards are provided as a free service to the boiler operations community to promote the free exchange of ideas and to provide assistance from one boiler operator to another as they see fit. 

Sprung Services accepts no responsibility nor guarantees the accuracy of any posts in these message boards.

Clock Time in the Forum by Wagner
To Whom It May Concern: It appears that the running clock time in these forums is off by one hour; ...
RE: Differential Settings on Operating Pressure Control by Wagner
Dear Reed: In response to your questions: The school boiler that I am operating did not have much ...
RE: Water Column by Reed
I'm glad it took me a while to get to this question and Bob beat me to it. The answer is better tha...
RE: boiler licensing juristictions by Reed
These would also be of interest (from Bob's link): (13) hot water heating and other hot liquid bo...
RE: Differential Settings on Operating Pressure Control by Reed
Richard, I think I see your concern here. First, I wouldn't worry about a stable steam pressure....
RE: Differential Settings on Operating Pressure Control by Wagner
Dear Reed: Thank you very much for the thorough reply to my question about setting the subtractive ...
RE: Differential Settings on Operating Pressure Control by Reed
Richard, First of all, I would like to apologize for not getting back to you for so long.  I...
RE: Water Column by RBob
Hi Steve: .433 pounds per square inch per foot of water. Another way: A 'column' of water that...
RE: boiler licensing juristictions by RBob
Hi Steve: I think that your question might better be worded as "What boilers are exempt from operat...
Water Column by stevenaudette
  In class we were given the value for a water column. 0.4433…??? I’m looking for the exa...
Sprung Services Public Forums
Subject: Low water cutout
Prev Next
You are not authorized to post a reply.

Author Messages
mbmUser is Offline
Novice Member
Novice Member
Posts:5

06/20/2007 8:00 PM  

We have a 630hp 140lb Blr, when performing low water cutout test, after it cuts out and when refilling the boiler restarts up at idle. I think it is required to be reset but our chief disagrees. 

ReedUser is Offline
Veteran Member
Veteran Member
Posts:462

06/20/2007 8:02 PM  

Your boiler is required to have 2 low water cutouts.  One may be included with your pump control and the other must be installed in another water column and be set at a lower level than the first one.

If you are talking about the 2nd low water cutout, then it must have a manual reset, so it shouldn't start back up by itself at all.

CSD-1 (ASME “Controls and Safety Devices” ), section CW-140; Requirements for Water Level Controls for High-Pressure Steam Boilers, part “b” states:

“Functioning of the lower of the two controls shall cause safety shutdown and lockout“

Although I'm not aware of code that specifically covers the issue, if you are testing the higher of the two cutouts (typically included in the operating float), then I believe the boiler can start back up automatically and having it start at low fire would make sense.  I will ask Joel to check this post over to see if he agrees with this.

If you need to buy a low-water cutout that includes a manual reset, let me know and I will get you a quote.  We are a McDonnell & Miller distributor.  We just don't have many of those entered into our web store yet.  We are typically the least expensive distributor by a pretty comfortable margin.

 

Reed


Reed Sprung
Sprung Services, Inc.
jamatoUser is Offline
Novice Member
Novice Member
Posts:9

06/20/2007 8:04 PM  

Excellent response Reed.  I couldn't have explained it better myself. 

The first LWCO may reset automatically, but the second must cause a shutdown and lock out.

Thanks,

 

Joel T. Amato

Chief Boiler Inspector

mbmUser is Offline
Novice Member
Novice Member
Posts:5

11/19/2007 6:54 AM  

OK, “Functioning of the lower of the two controls shall cause safety shutdown and lockout“. So if the higher of the two cuts it out and then the lower also becomes involved it’s still ok for it to restart? Only if the lower of the two is activated, by it’s self or first, that we get a lockout on our fire eye.  And this is OK? Still not sure.

ReedUser is Offline
Veteran Member
Veteran Member
Posts:462

11/19/2007 3:31 PM  

One of the low water cutouts must be of the manual reset type.  This means that if both low water cutouts have tripped/activated then your boiler must be manually reset before it can start.  If the low-water cutout without the manual reset capability trips but the other control does not it is OK for your boiler to start back up on it's own.

Basically:

*Your boiler can not restart itself if the low water cutout with the manual reset is tripped regardless of whether the other one trips or not.

*Your boiler must have at least one low water cutout with a manual reset.

*If "the lower also becomes involved" means the lower cutout trips, then no, you can not have your boiler reset itself in this case.

 

Does this answer the question, or am I not quite understanding your question?

-Reed

 


Reed Sprung
Sprung Services, Inc.