Your boiler is required to have 2 low water cutouts. One may be included with your pump control and the other must be installed in another water column and be set at a lower level than the first one.
If you are talking about the 2nd low water cutout, then it must have a manual reset, so it shouldn't start back up by itself at all.
CSD-1 (ASME “Controls and Safety Devices” ), section CW-140; Requirements for Water Level Controls for High-Pressure Steam Boilers, part “b” states:
“Functioning of the lower of the two controls shall cause safety shutdown and lockout“
Although I'm not aware of code that specifically covers the issue, if you are testing the higher of the two cutouts (typically included in the operating float), then I believe the boiler can start back up automatically and having it start at low fire would make sense. I will ask Joel to check this post over to see if he agrees with this.