NOTICE:

Information provided in these message boards is not necessarily the opinion of Sprung Services, Inc.  These discussion boards are provided as a free service to the boiler operations community to promote the free exchange of ideas and to provide assistance from one boiler operator to another as they see fit. 

Sprung Services accepts no responsibility nor guarantees the accuracy of any posts in these message boards.

Clock Time in the Forum by Wagner
To Whom It May Concern: It appears that the running clock time in these forums is off by one hour; ...
RE: Differential Settings on Operating Pressure Control by Wagner
Dear Reed: In response to your questions: The school boiler that I am operating did not have much ...
RE: Water Column by Reed
I'm glad it took me a while to get to this question and Bob beat me to it. The answer is better tha...
RE: boiler licensing juristictions by Reed
These would also be of interest (from Bob's link): (13) hot water heating and other hot liquid bo...
RE: Differential Settings on Operating Pressure Control by Reed
Richard, I think I see your concern here. First, I wouldn't worry about a stable steam pressure....
RE: Differential Settings on Operating Pressure Control by Wagner
Dear Reed: Thank you very much for the thorough reply to my question about setting the subtractive ...
RE: Differential Settings on Operating Pressure Control by Reed
Richard, First of all, I would like to apologize for not getting back to you for so long.  I...
RE: Water Column by RBob
Hi Steve: .433 pounds per square inch per foot of water. Another way: A 'column' of water that...
RE: boiler licensing juristictions by RBob
Hi Steve: I think that your question might better be worded as "What boilers are exempt from operat...
Water Column by stevenaudette
  In class we were given the value for a water column. 0.4433…??? I’m looking for the exa...
Sprung Services Public Forums
Subject: Thermostat
Prev Next
You are not authorized to post a reply.

Author Messages
DanielUser is Offline
Novice Member
Novice Member
Posts:4

02/16/2012 12:32 AM  

What does longer on the anticipator setting on a mercury switch thermostat mean?

Dan

RBobUser is Offline
Intermediate Member
Intermediate Member
Posts:31

02/16/2012 1:30 PM  
Hi Daniel:

Increasing the setting will cause the cycle time of the boiler/furnace to increase--or the cycles per hour to decrease.
Does that help?

BobH
ReedUser is Offline
Veteran Member
Veteran Member
Posts:462

02/16/2012 1:40 PM  

Imagine you have a house that heats up faster in a room other than the one the thermostat is in.  If you had no anticipator the furnace would stay on until the thermostat was warm enough (inside the thermostat) to shut the furnace off.  This could mean the rest of the house may be warmer than you intended  If you set the anticipator to a setting greater than 0, then the thermostat will shut off a little before reaching the setpoint.  This allows the heat from the other room to make it to the thermostat.

The anticipator works by allowing more current to flow through a resistor.  Adjusting the setting varies the amount of resistance.  The heat generated by this warms the coil that is normally used to shut the furnace off when it gets warm enough (and turn it on when it gets cold enough).  By adding more heat than is actually in the ambient air, it shuts the furnace off early. 

If set properly, an anticipator keeps the living space more comfortable and saves energy.

The image below shows the anticipator in the center.  The further the dial is set (clockwise) from the yellow wire, the greater the setting.







Reed Sprung
Sprung Services, Inc.
ReedUser is Offline
Veteran Member
Veteran Member
Posts:462

02/16/2012 1:43 PM  
Oops, Bob had that one I guess. Both of our answers are correct. I just went over the river and through the woods to get there.

Reed Sprung
Sprung Services, Inc.
You are not authorized to post a reply.



ActiveForums 3.7

You must be registered and logged in to post a question or reply to a question.  Registration is FREE!  There are more message boards at: SprungTraining.com.