Jeff,
Unless there is something REALLY wrong with the softener it shouldn't be causing a discoloration problem in the clothes. The softener's purpose is actually to remove hardness (minerals, salts, etc) from the water, not add salt and stain the water yellow.
Even if the softeners were adding something they shouldn't be, the boiler acts like a still. Unless there are other problems like carryover, salts and the like will accumulate in the boiler and will not leave with the steam.
That being said, have you or anyone else done a hardness test on the softeners? That would be a good place to start. Check that and post the results if you have time. TDS and pH tests may also be a good idea. A very high TDS could cause carryover which could foul a process like dry cleaning.
Are they using any type of water treatment chemicals?
If the boiler is short cycling every 30 seconds it may not be surprising that the component that starts/ignites the boiler is going bad early. It's tough to determine for sure, but I would focus on the short cycling issue and see if the igniter failure problem takes care of itself.
The operating pressuretrol should have an adjustment on it to control hunting. This is normally called the differential adjustment. Try increasing this (it would be the screw next to the adjustment screw for the set pressure). If the differential is 1 and the steam setupoint is 10, then the boiler shuts off at 10 and starts back up at 9 (psig). If the differential were set at 2 then the boiler would shut off at 10 and come back on at 8. Obviously, in this case you would want to set the differential as high as you can without causing an unacceptably low steam pressure before the boiler restarts. I would also adjust the set pressure as high as conditions permit so you have more room for a big differential.
If you can't adjust this so there is a reasonable time period before the boiler cycles then you may want to look at other things.
Is the burner capable of running at different firing rates or does it just shut off and turn on as needed? If it just shuts off and turns on in response to the load, then you may need a different control system and/or burner. Another thing that could help would be some type of accumulator or another small boiler to make the steam pressure drop slower.
-Reed |