Information provided in these message boards is not necessarily the opinion of Sprung Services, Inc.  These discussion boards are provided as a free service to the boiler operations community to promote the free exchange of ideas and to provide assistance from one boiler operator to another as they see fit. 

Sprung Services accepts no responsibility nor guarantees the accuracy of any posts in these message boards.

NOTICE:

Information provided in these message boards is not necessarily the opinion of Sprung Services, Inc.  These discussion boards are provided as a free service to the boiler operations community to promote the free exchange of ideas and to provide assistance from one boiler operator to another as they see fit. 

Sprung Services accepts no responsibility nor guarantees the accuracy of any posts in these message boards.

Clock Time in the Forum by Wagner
To Whom It May Concern: It appears that the running clock time in these forums is off by one hour; ...
RE: Differential Settings on Operating Pressure Control by Wagner
Dear Reed: In response to your questions: The school boiler that I am operating did not have much ...
RE: Water Column by Reed
I'm glad it took me a while to get to this question and Bob beat me to it. The answer is better tha...
RE: boiler licensing juristictions by Reed
These would also be of interest (from Bob's link): (13) hot water heating and other hot liquid bo...
RE: Differential Settings on Operating Pressure Control by Reed
Richard, I think I see your concern here. First, I wouldn't worry about a stable steam pressure....
RE: Differential Settings on Operating Pressure Control by Wagner
Dear Reed: Thank you very much for the thorough reply to my question about setting the subtractive ...
RE: Differential Settings on Operating Pressure Control by Reed
Richard, First of all, I would like to apologize for not getting back to you for so long.  I...
RE: Water Column by RBob
Hi Steve: .433 pounds per square inch per foot of water. Another way: A 'column' of water that...
RE: boiler licensing juristictions by RBob
Hi Steve: I think that your question might better be worded as "What boilers are exempt from operat...
Water Column by stevenaudette
  In class we were given the value for a water column. 0.4433…??? I’m looking for the exa...
Sprung Services Public Forums
Subject: Hydronic system venting/residential
Prev Next
You are not authorized to post a reply.

Author Messages
RBobUser is Offline
Intermediate Member
Intermediate Member
Posts:31

10/20/2009 3:14 PM  

Hey all-

I was just over at a friends (turn of the (last) century) house- w/ an upgraded (in the 70s-80s by the look of things) hydronic system + fin tube baseboard radiators.  They were complaining of no heat on the second floor.  Easy, right?  =bleed the radiators on the second floor.

Except there are no bleeds on the second floor.  I even hand-over-handed the whole system (except for the risers in the wall, of course )

Am I missing something big picture here?  I've always, always found bleeds in a hydronic system at the high point/furthest point.

The boiler has an auto bleed, but I don't think that that little pump is going to be able to move enough water to push air down to the basement to let it out there.

Thanks-

BobH

ReedUser is Offline
Veteran Member
Veteran Member
Posts:462

10/21/2009 6:23 PM  

Almost all systems have vents located in the discharge piping of the baseboard heater that you can see when you take the cover off of the heater.  I assume you looked there given your knowledge level.

That said, there are a few systems out there with no vents.  What are the safeties set at (normally 30 psig)?  What do you normally run the pressure at?  I would try the easy way first:

###1###

Run the pressure up as high as you are comfortable.  This might be 25 or 26# or so.  I wouldn't run it up this high if I suspect corroded piping in the system that may not take the abuse. 

Running the pressure higher will squeeze the air bubble in the baseboard heater and possibly allow some water flow through the unit.  If you can make this happen, the water will entrain the air and carry it down to the vent in the basement regardless of the size of the pump. 

If this is working, you will run the pressure up and then come back later.  The pressure should have come back down on it's own somewhat because of the air that has left the system.  If you still have no heat, run the pressure back up.

If the pressure stays high and this procedure doesn't restore heat, then:

###2###

Check the zone valves.  Push the manual open lever.  Do you hear flow?  Does the unit provide heat? (this will only work if the circulating pump is running)  Problems related to zone valves can be the zone valve motor, the valve itself may by locked up, the transformer used for control power may be bad, the thermostat could be bad, or there could be a bad circuit board.  Replace part as necessary.

I've listed the zone valve check as #2, but you could do it before trying to run the pressure up if it's easier with your system.  Do whichever you suspect or what is easiest first.

When you are done, put the pressure back to normal.  Normal pressure should be 0.433 X the height of the system in feet.  Then add 3 to 5 pounds for a margin for error.

If that doesn't work:

###3###

Check the vent in the basement.  Are you sure it's working?  If it isn't, the air in the system will accumulate at the top of the system.  This air may normally be entrained and carried down to the automatic vent.  If the automatic vent doesn't work, the air will just be carried back to the top of the system.

If you aren't sure, replacing this will probably involve unscrewing it and screwing a new one in, which would be easier than sweating new manual valves in at the baseboard heaters.

After replacing the automatic vent, repeat step #1.

If this doesn't work:

###4###

Is there only one circulating pump in the system?  My house has 5, and they aren't all right at the boiler.  Make sure you know how many there are and that they all work when they are supposed to.  Make sure you are hearing flow when any of the pumps are on.

Or:

###5###

Give up and sweat in manual bleeders.  Hopefully one of the above procedures will save you from this, although sweating in the bleeders isn't that difficult anyway.

-Reed

 


Reed Sprung
Sprung Services, Inc.
RBobUser is Offline
Intermediate Member
Intermediate Member
Posts:31

10/21/2009 8:54 PM  

Thanks, Reed--I knew I could count on you.  I couldn't for the life of me find a bleed up high...as there are none.   I've been trying to force the bubble down to the boiler, and it ain't going.  There's no real 'zones', there is  just an upstairs loop, and a downstairs loop--with balance valves.  I've tried just running the upper loop (Isolating the other with the balance valves..as well as producing a bit of hydraulic shock by slamming them... )--in hopes that that would push the bubble...but...no.  From the pieces of equipment scattered about the floor in the basement, they've replaced the original B+G pump with what looks like a little Taco.  I suspect that the replacement pump may have been chosen based on $, not specs.

I am thinking that a real nice, easy solution for this is going to be to just cut in a high point (auto) bleed. 

Thanks again-

BobH

ReedUser is Offline
Veteran Member
Veteran Member
Posts:462

10/21/2009 9:36 PM  

Has the system ever worked properly in it's current configuration?  The fact that you isolated the lower loop rules most things out and makes raising the pressure less likely to be a successful strategy. 

If you are going to put an autobleed in the top of the system, I would suggest replacing the one downstairs, and if that doesn't fix the problem, swap them back out and sweat the new one in upstairs.

 


Reed Sprung
Sprung Services, Inc.
BillUser is Offline
Chief Member
Chief Member
Posts:1035

10/22/2009 7:48 AM  

What kind of exspansion tank do you have on this system is it a bladder or and old tank. If it is and old tank make sure the system isn't isn't water bound.

RBobUser is Offline
Intermediate Member
Intermediate Member
Posts:31

10/22/2009 7:35 PM  

Thanks for the replies--I should state up front that the bulk of my real world experience is not in residential hydronics.

I was told that the system did, after the last time it was 'serviced' (several years ago), work.  For most of one winter.

There is an auto bleed on the boiler...encased in a mountain of lime--I hesitated to touch it, as I'm looking at this as a favour and don't need to be snapping corroded brass fittings off of the boiler at this point...

FWIW--The boiler fill valves lead down to the deck where a l'il expansion tank (?) 3-5 gals or so sits.  There's a complicated looking ball of brass that tees into the end of this tank.  I assumed that the ball o'brass is a check, but...who knows?  I didn't check them closed, as they too, are corroded...and look suspiciously like they are open...

I got about this far into it (no bleeds upstairs, and a quick look at the boiler), when I got a call from home and had to run.  If I (have to) go back, I'll report more.

I think that I need to check to ensure that the tank isn't waterlogged, and I need to replace the boiler bleed.  I'd like to add a high point auto bleed so  that I never have to go back there, too.

 

BobH

garykUser is Offline
Novice Member
Novice Member
Posts:2

04/17/2012 6:58 PM  
Is this post closed Think everyone is overlooking something very simple that I have applied to a handfull of home boiler systems that worked for all of them. It was a very cold week and no one could get there homes warm at all
RBobUser is Offline
Intermediate Member
Intermediate Member
Posts:31

04/17/2012 7:05 PM  

Hi Garyk:

I don't think that anything is ever really closed :)

I do know that I just ran away from that repair--I guess that I would have (if escape wasn't an option) put in a high point bleed, and then........but if you've got any input, I'm all ears--It's always nice to add to my treasure trove of knowledge.  Most of the time I end up saying "I know I heard of something like that...somewhere...I wonder what it was?"

 

BobH

BillUser is Offline
Chief Member
Chief Member
Posts:1035

04/18/2012 8:03 AM  

One thing you should look at is the circulating pump. If it is a small enclosed pump just because the motor is running doesn't mean the impeller is working. Should check this out do to all of the corrosion you were talking about.