Jeff,
The only possible problem with accuracy regarding your blowdown controller might be the size of the orifice in your blowdown line.
The orifice in your automatic blowdown line is sized to provide the right amount of flow @ 100 psig. If you only have 15 psig pushing water through the same orifice there may not be enough flow. This could cause the orifice to foul or you may just have problems getting enough blowdown to keep your TDS in line.
You will probably need to install an extra orifice in parallel with your current one. Set them up so one orifice is for high-pressure and the other is for low-pressure and you can isolate the one that isn't in use.
The electronics will still work just fine. The valve will open when conductivity is too high and shut when it's too low. The logic of your controller won't care what the pressure is.
You could calculate the size of the new orifice you'll need, but I would have to dig to come up with the formulas for you. Try checking the docs that came with the controller. If there is no chart showing the right size, just try one about twice as big as your current one. If your TDS is fine then stick with that size. If your conductivity creeps up over the weekend then increase the orifice size.
There are generally 3 different things to look at when you are converting your boiler to a HP/LP switchable system:
1. Get the boiler controls set up properly to meet state code (see my post here).
2. Is your piping big enough? In your case it is because you aren't using the steam for anything in the evenings or weekends.
3. Anything unusual. This would include the automatic blowdown issue. I can't think of anything else for your situation. Most of the big problems are usually out in the facility somewhere, which doesn't apply to you.
Hope this helps. Post again if you have any more questions.
Reed |