Information provided in these message boards is not necessarily the opinion of Sprung Services, Inc.  These discussion boards are provided as a free service to the boiler operations community to promote the free exchange of ideas and to provide assistance from one boiler operator to another as they see fit. 

Sprung Services accepts no responsibility nor guarantees the accuracy of any posts in these message boards.

NOTICE:

Information provided in these message boards is not necessarily the opinion of Sprung Services, Inc.  These discussion boards are provided as a free service to the boiler operations community to promote the free exchange of ideas and to provide assistance from one boiler operator to another as they see fit. 

Sprung Services accepts no responsibility nor guarantees the accuracy of any posts in these message boards.

Clock Time in the Forum by Wagner
To Whom It May Concern: It appears that the running clock time in these forums is off by one hour; ...
RE: Differential Settings on Operating Pressure Control by Wagner
Dear Reed: In response to your questions: The school boiler that I am operating did not have much ...
RE: Water Column by Reed
I'm glad it took me a while to get to this question and Bob beat me to it. The answer is better tha...
RE: boiler licensing juristictions by Reed
These would also be of interest (from Bob's link): (13) hot water heating and other hot liquid bo...
RE: Differential Settings on Operating Pressure Control by Reed
Richard, I think I see your concern here. First, I wouldn't worry about a stable steam pressure....
RE: Differential Settings on Operating Pressure Control by Wagner
Dear Reed: Thank you very much for the thorough reply to my question about setting the subtractive ...
RE: Differential Settings on Operating Pressure Control by Reed
Richard, First of all, I would like to apologize for not getting back to you for so long.  I...
RE: Water Column by RBob
Hi Steve: .433 pounds per square inch per foot of water. Another way: A 'column' of water that...
RE: boiler licensing juristictions by RBob
Hi Steve: I think that your question might better be worded as "What boilers are exempt from operat...
Water Column by stevenaudette
  In class we were given the value for a water column. 0.4433…??? I’m looking for the exa...
Sprung Services Public Forums
Subject: Proof of Closure Valves
Prev Next
You are not authorized to post a reply.

Author Messages
JeffGUser is Offline
Novice Member
Novice Member
Posts:7

06/20/2007 10:07 PM  

My boiler wouldn't light this morning and after troubleshooting it, I found no control power past the POC switch in one of the gas valves.  I have never had an issue with a POC valve much less never had to work on one, so I would like a little education on them.  To that end, pretty safe bet a POC valve is a safety to prevent raw gas from blowing through the boiler during pre-purge?  With my issue being the POC valve, what is the best way to test it to determine if it is a stuck switch or if the valve is indeed not closing?  My POC valve is a Seimens.  This happened once before about 4 months ago but as I and PBBS were troubleshooting it, she suddenly kicked in and began working, and we were not able to get it to fault out again, so we never did figure out what the cause of the shutdown was.  Any advice?  Thank you.

Cheers

 

Jeff Gardner - Plant Engineer - Heathcare Waste Solutions, Inc.

ReedUser is Offline
Veteran Member
Veteran Member
Posts:462

06/20/2007 10:07 PM  

Can you tell if the valve is shut all the way?


Reed Sprung
Sprung Services, Inc.
BFNKUser is Offline
Novice Member
Novice Member
Posts:1

06/20/2007 10:08 PM  

Siemens documentation states that POC valves are not adjustable and suggests replacing.

jamatoUser is Offline
Novice Member
Novice Member
Posts:9

06/20/2007 10:11 PM  

If the valve is not functioning properly the only entity that can repair or rebuild the valve is the original manufacturer.  If you attempt to repair or fix the valve, the valve is no longer UL listed, and this is a violation of state statute.

If this valve is not functioning properly it could cause a furnace explosion.

Replace the valve.

 

Joel T. Amato                                   

Chief Boiler Inspector

paulhUser is Offline
Novice Member
Novice Member
Posts:3

09/29/2010 5:54 PM  

Proof of closure switches in Maxon gas valves can be checked by seeing if the relief vent between the two gas vales is building pressure.

We do this on an annual basis because the first valve in line could leaking and you'll never know it, even if the proof of closure switch is made.